Some interesting tidbits.
I know this (trophy cases) came up a while back and here is what the doctor ordered regarding that.
Section 8.1.1(7)"Furniture, such as portable wardrobe units, cabinets, trophy cases and similar features not intended for occupancy, do not require sprinklers to be installed in them. This type of feature shall be permitted to be attached to the finished struture. This change is tied to a change in section 8.5.3.2.3 that requires the distance from the wall to the sprinkler to be measured to the wall behind furniture, such as: wardrobes, cabinets, and trophy cases."
And then there is this one.
Section 8.15.7 "Porte-cocheres were added to teh title of 8.15.7 and through the subsections. An annex note was added to clarify parking areas. A.8.15.7.2 states that vehicles that are temporarily parked are not considered storage. Areas located at drive-in bank windows or porte-cocheres at motels and hotels normally do not require sprinklers where there is no occopancy above, is entirely constructed of noncombustibnle, or limited combustible materials or fire retardant treated lumber, and is not the only means of egress. However, areas under exterior ceilings where the building is prinklered should be protected to to the occupancy above."
Ah, and finally this one which I dearly love. It is about time.
8.17.4.2.4 "The alarm test connection shal be permitted to be installed in any location on the fire sprinkler system downstream the water flow alarm. Supporting annex material was added as well to clarify that the alarm test connection is not required in the most remote location."
So do what I do, come right off the riser a couple feet or so above the flow switch.
I hope this helps some of you.
I know this (trophy cases) came up a while back and here is what the doctor ordered regarding that.
Section 8.1.1(7)"Furniture, such as portable wardrobe units, cabinets, trophy cases and similar features not intended for occupancy, do not require sprinklers to be installed in them. This type of feature shall be permitted to be attached to the finished struture. This change is tied to a change in section 8.5.3.2.3 that requires the distance from the wall to the sprinkler to be measured to the wall behind furniture, such as: wardrobes, cabinets, and trophy cases."
And then there is this one.
Section 8.15.7 "Porte-cocheres were added to teh title of 8.15.7 and through the subsections. An annex note was added to clarify parking areas. A.8.15.7.2 states that vehicles that are temporarily parked are not considered storage. Areas located at drive-in bank windows or porte-cocheres at motels and hotels normally do not require sprinklers where there is no occopancy above, is entirely constructed of noncombustibnle, or limited combustible materials or fire retardant treated lumber, and is not the only means of egress. However, areas under exterior ceilings where the building is prinklered should be protected to to the occupancy above."
Ah, and finally this one which I dearly love. It is about time.
8.17.4.2.4 "The alarm test connection shal be permitted to be installed in any location on the fire sprinkler system downstream the water flow alarm. Supporting annex material was added as well to clarify that the alarm test connection is not required in the most remote location."
So do what I do, come right off the riser a couple feet or so above the flow switch.