Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

NFPA 13 2013 Section 9.3.7.8 and Concrete Anchors

Status
Not open for further replies.

JasonBatts

Mechanical
Mar 23, 2017
4
thread184-362221 Good afternoon. This thread was closed but thought I'd chime in on the discussion as my company recently encountered this "new" issue. I posed the same question to the NFSA Engineer of the Day (EOD) and they concur, that ALL piping - either seismic bracing or just hanging 1" armovers - that are suspended from a concrete anchor within a seismic zone, that the anchor shall be in compliance with ACI 355.2. Upon further investigation, not only are Hilti's HDI and HDI-P not in compliance, but neither are their widely used in the PNW: Hilti HCI-WF Pre-Case Concrete insert, a.k.a. "banger". This was disconcerting to me as it's never been flagged by any AHJ until we worked on a USACOE project. Anyone know off the top of their head a pre-cast concrete insert that IS in compliance with this NFPA code?
 
Replies continue below

Recommended for you

I was going to say Powers makes an undercut listed for cracked concrete (complying with one of the ESR's), but I think they are DeWalt now. Just did a cast in place seismic job and spec'd the TZ's (the wedges mentioned in your linked post).

Here's a link to the DeWalt undercut:

 
A phonecall sometimes is so much easier. Hilti corrected me in that the Hilti HCI-WF, it does not need to comply with ACI 355.2 because it’s a Pre-Cast Anchor, and not Post-Installed: “ACI 355.2 Qualifications of Post-Installed Mechanical Anchors in Concrete and Commentary”.
 
Ahh. I thought you were asking about an anchor for precast concrete panels, not an insert that you set prior to the pour.
 