I have a 200'x200' building with a single slope roof having a 1/2" in 12" pitch.
Low side is 32'-8" to underside of deck.
High side is 41'-0" to underside of deck.
I need to use K22.4 pendant ESFR sprinklers @40 psi which covers us for Cartoned Nonexpanded plastics.
Problem I have is we might have Exposed Nonexpanded plastic and once we hit above 40'-0" in-rack sprinklers are required via the asterisk.
Except for 24'-0" near the high side wall most of the building is below 40'-0" which covers exposed nonexpanded plastic to a max height of 35' and would it be appropriate to tell the owner as long as he keeps the exposed non-expanded plastic commodity 39'-0" from the high end of the building?
We do NOT want to install inrack sprinklers.