What size and what is in the pipe ???????????
Not sure if you have two questions
1. what combustibles can be in a Type 1 A building??? I cannot answer that one
and/or
2. What does NFPA 13 say:::
this more then likely the answer:::
8.15.1.2* Concealed Spaces Not Requiring Sprinkler Protection.
8.15.1.2.1* Concealed spaces of noncombustible and limited-combustible construction with minimal combustible loading having no access shall not require sprinkler protection.
A.8.15.1.2.1 Minor quantities of combustible materials such as but not limited to: cabling, nonmetallic plumbing piping, non-structural wood, etc. can be present in concealed spaces constructed of limited or noncombustible materials but should not typically be viewed as requiring sprinklers (see 8.15.1.1). For example, it is not the intent of this section to require sprinklers, which would not otherwise be required, in the interstitial space of a typical office building solely due to the presence of the usual amount of cabling within the space. The threshold value at which sprinklers become necessary in the concealed space is not defined.
8.15.1.2.1.1 The space shall be considered a concealed space even with small openings such as those used as return air for a plenum.
8.15.1.2.2 Concealed spaces of noncombustible and limited-combustible construction with limited access and not permitting occupancy or storage of combustibles shall not require sprinkler protection.
3.3.13* Limited-Combustible (Material). Refers to a building construction material not complying with the definition of noncombustible material that, in the form in which it is used, has a potential heat value not exceeding 3500 Btu/lb (8141 kJ/kg), where tested in accordance with NFPA 259, Standard Test Method for Potential Heat of Building Materials, and includes either of the following: (1) materials having a structural base of noncombustible material, with a surfacing not exceeding a thickness of 1/8 in. (3.2 mm) that has a flame spread index not greater than 50; or (2) materials, in the form and thickness used, having neither a flame spread index greater than 25 nor evidence of continued progressive combustion, and of such composition that surfaces that would be exposed by cutting through the material on any plane would have neither a flame spread index greater than 25 nor evidence of continued progressive combustion, when tested in accordance with ASTM E 84, Standard Test Method of Surface Burning Characteristics of Building Materials, or ANSI/UL 723, Standard Test Method of Surface Burning Characteristics of Building Materials.