NFPA 13, section 8.15.4 Vertical Openings, specifies a draft stop of at least 18" deep.
1) Where do you measure this 18"? Do you measure it from the top of the ceiling? or do you measure it from the sprinkler discharge?
2) In addition, it specifies the horizontal requirements of sprinklers not more than 6 ft apart and 6in to 12in from the draft stop, but it does not specify the vertical distance in relation to the draft stop.
3) If there are structural steel beams (24" deep) that are installed around the perimeter of the vertical opening, can these steel beams be techincally be used as the draft stop? or do you need to install a draft stop attached to the steel beam? Will the steel geometry effect the sprinkler spray, draft curtain and the overall effectiveness?
I really appreciate any help and clarification.
Thank you!!
1) Where do you measure this 18"? Do you measure it from the top of the ceiling? or do you measure it from the sprinkler discharge?
2) In addition, it specifies the horizontal requirements of sprinklers not more than 6 ft apart and 6in to 12in from the draft stop, but it does not specify the vertical distance in relation to the draft stop.
3) If there are structural steel beams (24" deep) that are installed around the perimeter of the vertical opening, can these steel beams be techincally be used as the draft stop? or do you need to install a draft stop attached to the steel beam? Will the steel geometry effect the sprinkler spray, draft curtain and the overall effectiveness?