Hello,
Consider vertical openings between two levels that are not used for stairways or staircases and are not large openings (i.e. greater than 20' dimensions and area greater than 1000 square feet). NFPA 13 seems unclear whether closely spaced sprinklers and draft curtains are required in these cases.
In the NFPA 13 (2010) Handbook it states "closely spaced sprinklers are required around a vertical opening only when it would otherwise be required to be protected by a barrier by the building code or NFPA 101...Smaller vertical openings may be referred to in the local building code or NFPA 101 as communicating spaces or convenience openings. These spaces are not required to have a barrier around the opening perimeter (See Section 8.6, Vertical Openings, in NFPA 101 for more details)". It goes on to say "Escalator openings in department stores are examples of vertical openings that would not be considered a convenience opening or convenience space, and as a result they would be required by NFPA 101 to be enclosed to protect against vertical fire spread."
In cases where a portion of a floor area is "Open to Above" to an adjacent floor but the opening is not used for a moving stairway or staircase and is not a "Large Opening", are closely spaced sprinklers and draft curtains required?