This is why you must train your guys to keep within the scope.
I obtain this information from an article in the Fire Protection Contractor Magazine.
Loss: $12,000,000--What Happened?
Our contractor performed annual inspections at our shopping center. He had being doing so for years. The strip plaza was sprinklered, but the exterior overhang was not protected by sprinklers. The contractor used industry standard reports, but on several occasions the inspector made notes in the comments section that where outside the scope of NFPA 25. Items such as spacing of the heads, temperature ratings of heads, and the need to add a head in an area of the building, where added to the comments section. The inspector never noted the non-sprinklered exterior overhang in his reports. A fire started outside the building and traveled up the overhang into the roof. Building was destroyed.
The property insurance carrier for the store subrogated against the sprinkler contractor for failing to inform the non-sprinklered area. When the contractor argued that it was outside the scope of NFPA 25 the produced all past inspection reports with numerous comments that where also outside of NFPA 25.
The property carrier argued that the building owner saw the contractor as "the expert" and assume the report covered all areas and all inadequacies of the system.
This is why you have to be careful, make certification mandatory and make random stops at your client facilities to ensure your inspectors are on top of their game.
I obtain this information from an article in the Fire Protection Contractor Magazine.
Loss: $12,000,000--What Happened?
Our contractor performed annual inspections at our shopping center. He had being doing so for years. The strip plaza was sprinklered, but the exterior overhang was not protected by sprinklers. The contractor used industry standard reports, but on several occasions the inspector made notes in the comments section that where outside the scope of NFPA 25. Items such as spacing of the heads, temperature ratings of heads, and the need to add a head in an area of the building, where added to the comments section. The inspector never noted the non-sprinklered exterior overhang in his reports. A fire started outside the building and traveled up the overhang into the roof. Building was destroyed.
The property insurance carrier for the store subrogated against the sprinkler contractor for failing to inform the non-sprinklered area. When the contractor argued that it was outside the scope of NFPA 25 the produced all past inspection reports with numerous comments that where also outside of NFPA 25.
The property carrier argued that the building owner saw the contractor as "the expert" and assume the report covered all areas and all inadequacies of the system.
This is why you have to be careful, make certification mandatory and make random stops at your client facilities to ensure your inspectors are on top of their game.