NMCivil
Structural
- May 23, 2016
- 10
Hello, newly registered to the forum. I have a question regarding the minimum spacing of fire sprinklers (6') and the use of the baffle that is described in section 8.6.3.4.2. We have a pair of sprinklers that are approximately 4.5 feet apart. It appears as though a wall was intended to be installed between these sprinklers, but was left out for one reason or another. Our FPE is asking for a piece of sheet metal to hang from the suspended ceiling between these sprinklers. These are standard pendent sprinklers.
Does anyone have pictures of a fix for this situation? Or recommendations about what we should do? I'm concerned that 1) the sheet metal hanging from the ceiling won't meet the "solid and rigid material" requirement. 2) if installed at the midpoint between the sprinklers, the baffle will need to be substantially larger than the minimum 8"x6" and we could start having clearance concerns below the baffle.
The FPE also stated that anything closer than 4" to the sprinkler will be considered an obstruction.
Any help you can provide is greatly appreciated.
Does anyone have pictures of a fix for this situation? Or recommendations about what we should do? I'm concerned that 1) the sheet metal hanging from the ceiling won't meet the "solid and rigid material" requirement. 2) if installed at the midpoint between the sprinklers, the baffle will need to be substantially larger than the minimum 8"x6" and we could start having clearance concerns below the baffle.
The FPE also stated that anything closer than 4" to the sprinkler will be considered an obstruction.
Any help you can provide is greatly appreciated.