I´m designing a wet automatic sprinkler system for a emergency diesel generator plant room on a hydro power plant.
The respective code (NFPA 851) calls for a density of 0.25 on the generator room.
This room is 5.3mx4.5m = 24.2m2 (17.4´x 14.8´=256sqft).
Following NFPA 13 I´m interpreting that it should be designed as a Extra Hazard Group 1 (the generator diesel tank is under it).
My problem came from checking the sprinkler spacing requirements in NFPA 13 (2002-8.6.3.2.4) (1996-4.6.3.2 where small room provisions are mentioned.
I read the definition of "small room" but it only mentions Light Hazard ocupancies, so I want to know if the small room provisions can be used for Extra Hazard G1 "small room".
If I follow the "small room provisions", two sprinklers woud do fine, but if not, four would be needed (if I´m not too lost in the code).
Thanks a lot in advance, and a merry Xtmas and happy new year to all those who have made this NFPA forum a great tool in my job.
The respective code (NFPA 851) calls for a density of 0.25 on the generator room.
This room is 5.3mx4.5m = 24.2m2 (17.4´x 14.8´=256sqft).
Following NFPA 13 I´m interpreting that it should be designed as a Extra Hazard Group 1 (the generator diesel tank is under it).
My problem came from checking the sprinkler spacing requirements in NFPA 13 (2002-8.6.3.2.4) (1996-4.6.3.2 where small room provisions are mentioned.
I read the definition of "small room" but it only mentions Light Hazard ocupancies, so I want to know if the small room provisions can be used for Extra Hazard G1 "small room".
If I follow the "small room provisions", two sprinklers woud do fine, but if not, four would be needed (if I´m not too lost in the code).
Thanks a lot in advance, and a merry Xtmas and happy new year to all those who have made this NFPA forum a great tool in my job.