ziptron
Materials
- Dec 9, 2010
- 64
Hi Everyone,
Does anyone have any understanding or experience with why the NFPA choose such a large temperature gap between the max ceiling temperature allowed and what the "ordinary" sprinkler head can provide? Same goes for all sprinkler classifications and their MAX ceiling temperature.
When you look at the "ordinary" classification, it is a sprinkler head that ranges between 135F to 170F, however it can only be used in a place where max ceiling temperature is 100F. If you have a sprinkler head on the higher end of that "ordinary" scale, you're basically 70F above the max ceiling temperature allowed..
Is there some research out there that backs this up and explains the rational? Are sprinkler heads not all that precise and have wide range of temperatures at which they will discharge below their rating even though they may be very good at discharging above their rating.. and thus, is the NFPA and the general industry afraid of false/early discharges?
Maybe we should be allowing 170F sprinkler heads to be installed where ceiling temperatures max out at 150F?
Any insight/discussion would be much appreciated.
Thanks!
Does anyone have any understanding or experience with why the NFPA choose such a large temperature gap between the max ceiling temperature allowed and what the "ordinary" sprinkler head can provide? Same goes for all sprinkler classifications and their MAX ceiling temperature.
When you look at the "ordinary" classification, it is a sprinkler head that ranges between 135F to 170F, however it can only be used in a place where max ceiling temperature is 100F. If you have a sprinkler head on the higher end of that "ordinary" scale, you're basically 70F above the max ceiling temperature allowed..
Is there some research out there that backs this up and explains the rational? Are sprinkler heads not all that precise and have wide range of temperatures at which they will discharge below their rating even though they may be very good at discharging above their rating.. and thus, is the NFPA and the general industry afraid of false/early discharges?
Maybe we should be allowing 170F sprinkler heads to be installed where ceiling temperatures max out at 150F?
Any insight/discussion would be much appreciated.
Thanks!