For the purpose of this post I am using NFPA 13 2010 Edition as it was the one on my desk and within reach.
I was wondering if anyone could clarify for me when Table 8.3.2.5(c) "Ratings of Sprinklers in Specified Residential Areas" applys. My confusion stems from the fact that some items appear in both Table 8.3.2.5(a) and (c), but the requirements are different.
For example per Table 8.3.2.5(a) intermediate temperature heads are required within a 1' radius of a downward discharging diffuser or 2'6" semicylinder of a horizontal diffuser. Table 8.3.2.5(c) requires intermediate temperature sprinklers within 24" of any hot air diffuser.
Consider this question in the context of a multiple "residential" unit building, such as a condo high-rise or a college dorm, where you have multiple dwelling units and common/areas. The individual units could be protected with either commercial or residential sprinkler heads depending on room size and available water, halls and common areas are protected with commercial heads.
Does Table 8.3.2.5(a) apply to the commercial heads and Table 8.3.2.5(c) apply to the residential heads? Or does Table 8.3.2.5(a) apply in the common areas and Table 8.3.2.5(c) apply in the dwelling units regardless of head type? I haven't gotten a strong opinion from the more senior designers that I have asked so far, and my web searches tend to return hits for write ups about specific individual temperature requirements rather than a higher level view of when to apply each table. Thought I would come here for another opinion.
Thank You
Huey
For the purpose of this post I am using NFPA 13 2010 Edition as it was the one on my desk and within reach.
I was wondering if anyone could clarify for me when Table 8.3.2.5(c) "Ratings of Sprinklers in Specified Residential Areas" applys. My confusion stems from the fact that some items appear in both Table 8.3.2.5(a) and (c), but the requirements are different.
For example per Table 8.3.2.5(a) intermediate temperature heads are required within a 1' radius of a downward discharging diffuser or 2'6" semicylinder of a horizontal diffuser. Table 8.3.2.5(c) requires intermediate temperature sprinklers within 24" of any hot air diffuser.
Consider this question in the context of a multiple "residential" unit building, such as a condo high-rise or a college dorm, where you have multiple dwelling units and common/areas. The individual units could be protected with either commercial or residential sprinkler heads depending on room size and available water, halls and common areas are protected with commercial heads.
Does Table 8.3.2.5(a) apply to the commercial heads and Table 8.3.2.5(c) apply to the residential heads? Or does Table 8.3.2.5(a) apply in the common areas and Table 8.3.2.5(c) apply in the dwelling units regardless of head type? I haven't gotten a strong opinion from the more senior designers that I have asked so far, and my web searches tend to return hits for write ups about specific individual temperature requirements rather than a higher level view of when to apply each table. Thought I would come here for another opinion.
Thank You
Huey