Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations GregLocock on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

NFPA 13D 1999

Status
Not open for further replies.

mitcham

Mechanical
Jun 28, 2003
16
Currently I am working on a one family 4-story dwelling project. The design has to comply with 13D 1999. I only have 13D 1996 handy. Are these two any different in terms of residential sprinkler spacing and locations. Can you please highlight the differences?

Regards
 
Replies continue below

Recommended for you

biggest difference is the listing of the sprinklers. You will need to use the datasheets for the current head listings...all of the residential flows changed on July 12, 2002. The old flow rates were based on 0.03 gpm / sq ft, now they are based on 0.05 gpm/ sq ft.

spacing is still basically the same...make sure if you leave heads out of the bathroom that you know to include the shower in the area of the bathroom. That may have been a change from 99 - 2002.

Hope this helps.
 
mfpd

I would like to thank you for your reply.



 
Status
Not open for further replies.

Part and Inventory Search

Sponsor