twd22285
Specifier/Regulator
- Jul 31, 2007
- 73
In NFPA 13D 2007 edition, under 8.2.5.2.1 it states as follows: Pendent sprinklers shall be located at least 3 feet away from obstructions such as ceiling fans and light fixtures unless the requirements of 8.2.5.4 are met. 8.2.5.4 gives you the table to refer to at 8.2.5.4.2(position of sprinkler to avoid obstructions to discharge). in my case i have a surface mount light that will be coming down 6" off the ceiling, my sprinkler head deflector will be an inch below the ceiling. If i were to follow that table i would have to be a minimum of 4' away from the light where as 8.2.5.2.1 tells me 3' away is ok. I have several issues with the way this is worded and the clarity, or lack there of, thats given. #1, does this refer to all lights even if it is a recessed mount light fixture where no obstruction is created. And if thats the case then why even put 8.2.5.2.1 in nfpa 13d. #2, it does not say when one over rules the other. #3, does the light fixture have to act as a continuos obstruction in order for the table (8.2.5.4.2) to apply. this paticular project i am working on is very large for a 13d application (30,000 sq. ft home) so if i have to go four feet away from the fixtures, instead of three, it will raise the cost of the project considerably. Any clarification is much appreciated. Thank you in advance.
tony
tony