cupcars
Mechanical
- Feb 26, 2002
- 19
4-story wood structure hotel with no retail or public spaces such as a restaurant or bar.
Building Official says the whole building has to be an NFPA 13 system because breakfast seating area
is considered "Assembly" and there is no horizontal fire barrier between the first & second floor.
They do have exceptions such as sqft & occupancy load. I believe
their max area was 735 sqft (15 sqft per person x 49 max occupancy load = 735 sqft) so their
solution was to make the breakfast area's smaller than 735 sqft, then it could be an NFPA 13R system.
I argued that this breakfast seating area is just part of a hotel.
They were not interested in what NFPA 13R says in Annex A (A.1.1)
THIS IS WHAT THEIR GOING BY:
SECTION 303 ASSEMBLY GROUP A
303.1 Assembly Group A. Assembly Group A occupancy includes, among others, the use of a building or structure, or a portion thereof, for the gathering of persons for purposes such as civic, social or religious functions; recreation, food or drink consumption or awaiting transportation.
Exceptions:
1. A building or tenant space used for assembly purposes with an occupant load of less than 50 persons shall be classified as a Group B occupancy.
2. A room or space used for assembly purposes with an occupant load of less than 50 persons and accessory to another occupancy shall be classified as a Group B occupancy or as part of that occupancy.
3. A room or space used for assembly purposes that is less than 750 square feet (70 m2) in area and accessory to another occupancy shall be classified as a Group B occupancy or as part of that occupancy.
4. Assembly areas that are accessory to Group E occupancies are not considered separate occupancies except when applying the assembly occupancy requirements of Chapter 11.
5. Accessory religious educational rooms and religious auditoriums with occupant loads of less than 100 are not considered separate occupancies.
Assembly occupancies shall include the following:
A-2 Assembly uses intended for food and/or drink consumption including, but not limited to:
Banquet halls
Night clubs
Restaurants
Taverns and bars
BUT THEN YOU HAVE THIS:
903.2.1.2 Group A-2. An automatic sprinkler system shall be provided for Group A-2 occupancies where one of the following conditions exists:
1. The fire area exceeds 5,000 square feet (464 m2).
2. The fire area has an occupant load of 100 or more.
3. The fire area is located on a floor other than a level of exit discharge serving such occupancies.
My question: Is the breakfast seating area really considered a part of the assembly code (IBC 303.1 Group A-2) or
should the space be incidental to the residential (R2) that the building is.
I've designed many NFPA 13R Hotels and this is a first...
Thanks!!
JC
Building Official says the whole building has to be an NFPA 13 system because breakfast seating area
is considered "Assembly" and there is no horizontal fire barrier between the first & second floor.
They do have exceptions such as sqft & occupancy load. I believe
their max area was 735 sqft (15 sqft per person x 49 max occupancy load = 735 sqft) so their
solution was to make the breakfast area's smaller than 735 sqft, then it could be an NFPA 13R system.
I argued that this breakfast seating area is just part of a hotel.
They were not interested in what NFPA 13R says in Annex A (A.1.1)
THIS IS WHAT THEIR GOING BY:
SECTION 303 ASSEMBLY GROUP A
303.1 Assembly Group A. Assembly Group A occupancy includes, among others, the use of a building or structure, or a portion thereof, for the gathering of persons for purposes such as civic, social or religious functions; recreation, food or drink consumption or awaiting transportation.
Exceptions:
1. A building or tenant space used for assembly purposes with an occupant load of less than 50 persons shall be classified as a Group B occupancy.
2. A room or space used for assembly purposes with an occupant load of less than 50 persons and accessory to another occupancy shall be classified as a Group B occupancy or as part of that occupancy.
3. A room or space used for assembly purposes that is less than 750 square feet (70 m2) in area and accessory to another occupancy shall be classified as a Group B occupancy or as part of that occupancy.
4. Assembly areas that are accessory to Group E occupancies are not considered separate occupancies except when applying the assembly occupancy requirements of Chapter 11.
5. Accessory religious educational rooms and religious auditoriums with occupant loads of less than 100 are not considered separate occupancies.
Assembly occupancies shall include the following:
A-2 Assembly uses intended for food and/or drink consumption including, but not limited to:
Banquet halls
Night clubs
Restaurants
Taverns and bars
BUT THEN YOU HAVE THIS:
903.2.1.2 Group A-2. An automatic sprinkler system shall be provided for Group A-2 occupancies where one of the following conditions exists:
1. The fire area exceeds 5,000 square feet (464 m2).
2. The fire area has an occupant load of 100 or more.
3. The fire area is located on a floor other than a level of exit discharge serving such occupancies.
My question: Is the breakfast seating area really considered a part of the assembly code (IBC 303.1 Group A-2) or
should the space be incidental to the residential (R2) that the building is.
I've designed many NFPA 13R Hotels and this is a first...
Thanks!!
JC