nubrun
Specifier/Regulator
- Apr 12, 2013
- 1
Good morning all,
I am a mechanical engineer that has recently been drug into managing a FS project (not the engineer of record) and have come across a question that seems to be vague. I read through the last 10 pages of this forum and didn't find anything so here goes my question.
Project information:
1. 3 story concrete dormitory building
2. Providing a wet-pipe FS system throughout the building
3. Dorm rooms are 8x15 feet or so concrete construction with no ceiling, but exposed concrete beam that splits the room in half, so two sprinklers will be required.
Are upright fire sprinklers acceptable for inside of the dorm rooms? It seems like the code sort of contradicts itself (I am no expert though)
According to the 2010 NFPA 13 section A8.10.2 it seems like if there are not listed res sprinklers, that quick-response sprinklers would be acceptable.
According to the 2002 NFPA 13R Section 6.6.7.1.1 Listed res sprinklers shall be used unless the dwelling unit is considered a compartment. Looking at the definition of a compartment, could the dorm dwelling units be considered a compartment? There is more than a 8" lintel.
I appreciate any help you can offer. I give you FP guys a lot of credit, just keeping up with these codes seems like a nightmare.
Thanks.
I am a mechanical engineer that has recently been drug into managing a FS project (not the engineer of record) and have come across a question that seems to be vague. I read through the last 10 pages of this forum and didn't find anything so here goes my question.
Project information:
1. 3 story concrete dormitory building
2. Providing a wet-pipe FS system throughout the building
3. Dorm rooms are 8x15 feet or so concrete construction with no ceiling, but exposed concrete beam that splits the room in half, so two sprinklers will be required.
Are upright fire sprinklers acceptable for inside of the dorm rooms? It seems like the code sort of contradicts itself (I am no expert though)
According to the 2010 NFPA 13 section A8.10.2 it seems like if there are not listed res sprinklers, that quick-response sprinklers would be acceptable.
According to the 2002 NFPA 13R Section 6.6.7.1.1 Listed res sprinklers shall be used unless the dwelling unit is considered a compartment. Looking at the definition of a compartment, could the dorm dwelling units be considered a compartment? There is more than a 8" lintel.
I appreciate any help you can offer. I give you FP guys a lot of credit, just keeping up with these codes seems like a nightmare.
Thanks.