Luis Bernal
Mechanical
- May 19, 2020
- 5
Hello,
Just looking to see if anyone has accomplish this testing
As per NFPA-14, 2013 Edition section 7.8.1 "The hydraulically designed standpipe system shall be designed to provide the water flow rate required by section 7.10 at a minimum residual pressure of 100 psi at the outlet of the hydraulically most remote 2-1/2" hose connection and 65 psi at the outlet of the hydraulically most remote 1-1/2" hose station." and a total water demand of 500 gpm from the most remote two valves and 250 gpm from all other standpipes up to 1000 gpm for sprinklered and 1250 gpm for non sprinklered buildings. The expectation in the test is same, the standpipes should be able to supply the required total flow simultaneously and one most remote outlet should provide 100 psi pressure. Therefore all the hose valves should be flown at the same time when testing. The test methodology suggested in NFPA 25 Handbook reflects the same requirement.
Given in my scenario I have PRV valves up to 4th floor on a 10 story building.
Most of these PRV have a good 40's to 50's PSI Loss through the calculation process.
AHJ is addressing that the same test done at the roof (most remote valves) should be done at the most remote valves with PRVs
in this case
(2) valves one at the 3rd (250gpm) Floor and one at the 4th (250gpm @ 100psi) most remote standpipe
additional which will be the 4th floor (250gpm) of the additional standpipe.
I just cant seem to get this to work flowing with the additional losses and pressure provided by the PRV manufacturer.
Im open to ideas or suggestions.
THANK YOU,
Just looking to see if anyone has accomplish this testing
As per NFPA-14, 2013 Edition section 7.8.1 "The hydraulically designed standpipe system shall be designed to provide the water flow rate required by section 7.10 at a minimum residual pressure of 100 psi at the outlet of the hydraulically most remote 2-1/2" hose connection and 65 psi at the outlet of the hydraulically most remote 1-1/2" hose station." and a total water demand of 500 gpm from the most remote two valves and 250 gpm from all other standpipes up to 1000 gpm for sprinklered and 1250 gpm for non sprinklered buildings. The expectation in the test is same, the standpipes should be able to supply the required total flow simultaneously and one most remote outlet should provide 100 psi pressure. Therefore all the hose valves should be flown at the same time when testing. The test methodology suggested in NFPA 25 Handbook reflects the same requirement.
Given in my scenario I have PRV valves up to 4th floor on a 10 story building.
Most of these PRV have a good 40's to 50's PSI Loss through the calculation process.
AHJ is addressing that the same test done at the roof (most remote valves) should be done at the most remote valves with PRVs
in this case
(2) valves one at the 3rd (250gpm) Floor and one at the 4th (250gpm @ 100psi) most remote standpipe
additional which will be the 4th floor (250gpm) of the additional standpipe.
I just cant seem to get this to work flowing with the additional losses and pressure provided by the PRV manufacturer.
Im open to ideas or suggestions.
THANK YOU,