sfallows
Specifier/Regulator
- Oct 18, 2007
- 45
This is a question about which hose connections are required to flow on the most remote standpipe. One party is arguing that you calc the top two as defined by the top hose valve + the testing hose valve while the other party defines it as the top two excluding the testing valve (as in the top two floors in this case)
On a Class I system per NFPA 14 2007 it requires "the minimum flow rate for the hydraulically most remote standpipe shall be 500 gpm, and the calculations proeedure sall be in accordance with 7.10.1.2" (7.10.1.1.1)
7.10.1.2 says in 7.10.1.2.1 "hydraulic calcs and pipe sizes for each standpipe shall be based on providing 250 gpm at the two hydraulically most remote hose connections on the standpipe and at the topmost outlet of each of the other standpipes at the minimum residual pressure required by section 7.8"
lastly 7.3.2.2 "An additional 2-1/2" hose connection shall be provided at the hydraulically most remote portion of the system to facilitate testing"
Anyone see anything that dictates which method is correct. While I understand that flowing the testing valve and the one next to it will be the most demanding, the placement (location) of said testing valve is determined by calculated hydraulic demand.
On a Class I system per NFPA 14 2007 it requires "the minimum flow rate for the hydraulically most remote standpipe shall be 500 gpm, and the calculations proeedure sall be in accordance with 7.10.1.2" (7.10.1.1.1)
7.10.1.2 says in 7.10.1.2.1 "hydraulic calcs and pipe sizes for each standpipe shall be based on providing 250 gpm at the two hydraulically most remote hose connections on the standpipe and at the topmost outlet of each of the other standpipes at the minimum residual pressure required by section 7.8"
lastly 7.3.2.2 "An additional 2-1/2" hose connection shall be provided at the hydraulically most remote portion of the system to facilitate testing"
Anyone see anything that dictates which method is correct. While I understand that flowing the testing valve and the one next to it will be the most demanding, the placement (location) of said testing valve is determined by calculated hydraulic demand.