Floks,
Our plant is designed with electrical and back up diesel pump.
According to NFPA 20 should we Connect the electrical one to UPS in addition to a national grid (reliable source) or only to the latest one (no need to UPS connection)

Regards
 
Replies continue below

Recommended for you

IMO, to have the diesel pump as the back-up, the electrical pump is okay with the regular power without UPS. And, it's still a good practice to have a double bus per supply circuit for the Fire water pump.
And, the Local AHJ has the final approval of your the fire water pump system.
 