NFPA 20 Number & Size of hose valves on test header? 1

Status
Not open for further replies.

ContractorDave

Mechanical
Jan 16, 2007
364
NFPA 20, table 5.25 lays out the test header valve configuration, but specifies 'centrifugal' pumps. Any thoughts as to why this is, or is this table be used for all types of fire pumps?

Regards
Dave
 
Replies continue below

Recommended for you

Also, there is the matter of the 200psi hydrostatic test required by 13R.

Regards
Dave
 
because it is under the general heading::::::


5.25 Summary of Centrifugal Fire Pump Data.



5.19.3.1* General.
5.19.3.1.1 Hose valves shall be listed.
5.19.3.1.2 The number and size of hose valves used for pump testing shall be as specified in Section 5.25.


2007 version
 