I am in need of a fire pump history lesson.
In the past two weeks, I have looked at two separate fire pump installations where 2,000gpm pumps had been installed with 8" suction and discharge piping, instead of the minimum 10" piping required by NFPA 20. The first time, I was quick to point it out as an error - but the second time, I started to wonder if it was more than just a coincidence.
Both pumps were installed in the early 80's, meaning that the design would have been governed by an early-to-mid 70's edition of NFPA 20. The oldest edition of 20 I have access to is '87, which lists minimum suction and discharge piping as 10" for a 2,000gpm pump.
Was there ever a time when NFPA 20 permitted 8" piping for 2,000gpm pumps?
Thanks in advance.
In the past two weeks, I have looked at two separate fire pump installations where 2,000gpm pumps had been installed with 8" suction and discharge piping, instead of the minimum 10" piping required by NFPA 20. The first time, I was quick to point it out as an error - but the second time, I started to wonder if it was more than just a coincidence.
Both pumps were installed in the early 80's, meaning that the design would have been governed by an early-to-mid 70's edition of NFPA 20. The oldest edition of 20 I have access to is '87, which lists minimum suction and discharge piping as 10" for a 2,000gpm pump.
Was there ever a time when NFPA 20 permitted 8" piping for 2,000gpm pumps?
Thanks in advance.