Hi,
Im trying to comply with the 25% drop in residual\static specified in NFPA 219 when carrying out hydrant flow testing. example below
Remote static 158 psi
hydrant 1 open with residual 154psi and flow 2627 lpm
hydrant 2 open with residual 140psi and total flow (x2 hyds)4735 lpm
hydrant 3 open with residual 116psi and total flow (x3 hyds)6545 lpm
total flow 6545 x (158-20)0.54 / (158-116)0.54 = 6545 x 138 0.54/42 0.54 = 9320 lpm Is this correct?
also
if I had a fire pump with a gauge that showed 170psi and the pump gauge drops whilst opening the hydrants, should I include this in my theoretical calc? if so how?
Thanks for any help