carletes
Chemical
- Jan 28, 2003
- 79
Dear all!
I am dealing with the sizing of the required capacity of the impoundment (diked) area around two crude oil storage tanks. I know that according to NFPA 30 it must be as a minimum equal to the largest tank volume. My question regards to the fire fighting water storage. I thought that during a ground fire the diking drain valves must be closed, so I think that impoundment capacity should be able to store not only crude oil from the tank but this fire fighting water as well. Why NFPA do not consider a bigger required capacity to consider the fire fighting water collection? Perhaps the drain valves of the diking must be open during a fire in order to drain water+hydrocarbons and in this way minimize the risk of fire extending to other tanks?
Thank you for any help.
I am dealing with the sizing of the required capacity of the impoundment (diked) area around two crude oil storage tanks. I know that according to NFPA 30 it must be as a minimum equal to the largest tank volume. My question regards to the fire fighting water storage. I thought that during a ground fire the diking drain valves must be closed, so I think that impoundment capacity should be able to store not only crude oil from the tank but this fire fighting water as well. Why NFPA do not consider a bigger required capacity to consider the fire fighting water collection? Perhaps the drain valves of the diking must be open during a fire in order to drain water+hydrocarbons and in this way minimize the risk of fire extending to other tanks?