ChrisConley
Mechanical
- May 13, 2002
- 975
I have a client with a Fibre Glass manufacturing facility. (Styrene Cross-Linked Composites Manufacturing). They've been tagged by the fire inspector as being deficient in NFPA 33 and some items of the Canadian National Fire Code.
My two questions are:
NFPA 33 calls for sprinkler protection in resin application areas for at least Ordinary Hazard, Group 2. Does this apply in a building does not require sprinkler protection? There is a fire protection system in place, but it isn't NFPA 13.
NFPA 33 calls for ventilation to reduce the concentration of the sprayed product to 25% of the LEL. The explanatory annex says: Tests of resin application areas have shown that the processes do not produce vapors that exceed 25% of the LEL. Resin application tests have also indicated that the maximum levels of vapor concentration are about 690 ppm for spray applications. The test were conducted in an enclosed area with no ventilation.
That sounds like no ventilation is actually required (other than the obvious).
I'd appreciate any input anyone has on NFPA 33 and Styrene Spray Booths.
My two questions are:
NFPA 33 calls for sprinkler protection in resin application areas for at least Ordinary Hazard, Group 2. Does this apply in a building does not require sprinkler protection? There is a fire protection system in place, but it isn't NFPA 13.
NFPA 33 calls for ventilation to reduce the concentration of the sprayed product to 25% of the LEL. The explanatory annex says: Tests of resin application areas have shown that the processes do not produce vapors that exceed 25% of the LEL. Resin application tests have also indicated that the maximum levels of vapor concentration are about 690 ppm for spray applications. The test were conducted in an enclosed area with no ventilation.
That sounds like no ventilation is actually required (other than the obvious).
I'd appreciate any input anyone has on NFPA 33 and Styrene Spray Booths.