NFPA 409 Design Pump Capacity

Status
Not open for further replies.

worravit

Petroleum
Oct 1, 2013
3
Dear All

I have question about design of fire water pump in Hangar NFPA 409
Refer from hydrauliac calculation, system is designed 6000 GPM @ 7 barg. So vendor select both pump, 3,000 GPM for each pump. But in my understand, the system should design for 6000 GPM for each pump or not?

Best Regards
WVt
 
Replies continue below

Recommended for you

NFPA 409-04 6.2.10.8.2 The total pumping capacity shall be such that maximum demand can be met with the largest fire pump out of service.

If you were going to use a 6,000 usgpm pump, you would be correct in that NFPA 409 would require a redundant backup.

Keep in mind that NFPA 20 requires a fire pump be able to flow at least 150% of it's rated capacity. For a 6,000 usgpm pump, that would be 9,000 usgpm (slightly overkill). You would probably be better off installing something like four 1,500 usgpm pumps in parallel. 1,500*1.5 = 2,250 usgpm @ 150% capacity. With the 4th pump as a redundant backup you would have 3*2,250 = 6,750 usgpm available (which works out to 133% of each pump's rated capacity)

NFPA 20-2010 4.8.3 also requires that centrifugal fire pumps with ratings over 5,000 usgpm must be subject to individual review by either the AHJ or a listing laboratory.
 