Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

NFPA 664 - Wood Processing & wood working facilities 1

Status
Not open for further replies.

MechGuy22

Mechanical
Jun 8, 2010
51
Hello everyone. I wanted to get some opinions on this. We have a wood working/metal working shop that is part of a much larger building. The total shop area is about 1600 ft^2.

According to NFPA 664 chapter 1, standard 664 only applies to shops over 5,000 ft^2. Does this mean that if the shop is less then 5000 ft^2 a dust collection system is not required at all? Or is this just saying that it doesen't have to comply with NFPA 664 if it is less than 5000 ft^2?

Thanks everyone.
 
Replies continue below

Recommended for you

NFPA 664 applies to your building because its area is greater than 5,000 square feet. NFPA 664 is concerned with the accumulation of wood flour over a building area larger than 5,000 square feet. If your client can't control the hazard, then the potential for a dust explosion could possibly be created by your client.

You may read about this hazard in an article I wrote several years ago and I attached to this message. Good luck.
 
 http://files.engineering.com/getfile.aspx?folder=294156de-5847-4683-b1f1-38af499f27eb&file=dust_deflagrations.pdf
Thank you for your reply, as well as the uploaded file.
 