Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations GregLocock on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

NFPA-704 diamond symbols on Storage Tanks

Status
Not open for further replies.

MJCronin

Mechanical
Apr 9, 2001
5,087
to all,

NFPA - 704 has labeling requirements for storage tanks. (i.e. the commonly found "diamond" symbols)

What governing legal authority requires the use of such symbols ?Is it the local fire marshal or perhaps the insurance carrier ?

Is it necessary to place new NFPA-704 lables on older existing tanks that never required such labels ?

Anyone with experience in this area ?

-MJC

 
Replies continue below

Recommended for you

normaly local ahj and yes we try to get older installations to add them, and can be required on existing
 
Chapter 5 of NFPA 30 and IFC Chapter 27 grants the AHJ the authority to require NFPA 704 hazard diamonds be installed on aboveground storage tanks and buildings.

The requirement is a general provision in both documents so it can be required at anytime on any existing or new installation.
 