mpparent
Electrical
- Sep 26, 2001
- 399
All,
Hopefully someone familiar w/ this subject can answer. Firstly, the arc flash calcs. in the NFPA are incomplete in my opinion, in that if you have a fault current level below 16kA(the equations are only good from 16kA to 50kA), how do you calculate quantities for values under 16kA?(I'm speaking specifically of the "distance for curable burn" calculation). Also, when calculating incident energy, it's only dependent upon the amount of short circuit current available. I would have thought that the system voltage would be a variable, since, for instance, 13.2kV fault can be sustained much easier than a 480V fault. I'm not really believing the numbers I'm getting. Thanks in advance,
Mike
Hopefully someone familiar w/ this subject can answer. Firstly, the arc flash calcs. in the NFPA are incomplete in my opinion, in that if you have a fault current level below 16kA(the equations are only good from 16kA to 50kA), how do you calculate quantities for values under 16kA?(I'm speaking specifically of the "distance for curable burn" calculation). Also, when calculating incident energy, it's only dependent upon the amount of short circuit current available. I would have thought that the system voltage would be a variable, since, for instance, 13.2kV fault can be sustained much easier than a 480V fault. I'm not really believing the numbers I'm getting. Thanks in advance,
Mike