We operate a fleet of diesel generators. Most of these generators utilize two 12 Volt batteries in series to provide 24 VDC starting power at approximately 400 Amps continuous cranking current. The batteries are rated at 190 Amp Hours (20 hour rating) with 1300 cold cranking amps.
We recently completed an NFPA 70E arc flash hazard analysis and were told by the engineer conducting the survey that our batteries meet the requirements of NFPA 70E article 320 (Batteries and Battery Rooms). It seems to me that the intent of article 320 is to cover larger battery installations, such as large commercial UPS installations. (It states that any battery with more than 1 KWH of storage is covered)
The hazard associated with starting batteries certainly warrants caution, but according to the analysis done, we have to wear a 20 cal/cm2 suit just to work near the batteries (due of course to electrical arc flash hazard, not chemical hazard).
Something about this just doesn't sound quite right. If this is truly the requirement, we will certainly abide by it, but I want to make sure that we are not mis-applying the intent of the NFPA 70E article 320 standard and creating an undue burden on those working on this equipment.
If anyone else has been down this road, your assistance will be greatly appreciated.
We recently completed an NFPA 70E arc flash hazard analysis and were told by the engineer conducting the survey that our batteries meet the requirements of NFPA 70E article 320 (Batteries and Battery Rooms). It seems to me that the intent of article 320 is to cover larger battery installations, such as large commercial UPS installations. (It states that any battery with more than 1 KWH of storage is covered)
The hazard associated with starting batteries certainly warrants caution, but according to the analysis done, we have to wear a 20 cal/cm2 suit just to work near the batteries (due of course to electrical arc flash hazard, not chemical hazard).
Something about this just doesn't sound quite right. If this is truly the requirement, we will certainly abide by it, but I want to make sure that we are not mis-applying the intent of the NFPA 70E article 320 standard and creating an undue burden on those working on this equipment.
If anyone else has been down this road, your assistance will be greatly appreciated.