raithrovers1
Industrial
- Feb 10, 2009
- 85
I am trying to come up with a definitive answer to what PPE is required for my technicians to use when taking voltage measurements on a 480VAC input UPS less than 100KVA with a nominal 120VDC buss. Looking at the NFPA 70E tables it states that that panelboards or other electrical equipment rated >240Vac and up to 600VAc require arc flash category 2 PPE. There is then a note at the bottom of the table that says "for equipment rated 600VAC or less, and protected by upstream current limiting fuses or current limiting circuit breakers sized at 200A or less, the arc flash PPE category can be reduced by 1".
My conclusion is that my technicians will only need level 1 PPE when taking measurements inside a 480Vin, 120VDC buss 100KVA or less UPS. My only concern is what constitutes a current limiting circuit breaker. This seems to be a UL classification but I can't find a definitive answer.
Any help as always will be appreciated.