I am trying to get some opinions on the arc flash hazard identification from Table 130.7(C)(15)(A)(a) in the 2015 NFPA 70E
The task I am most interested in is: Opening voltage transformer or control power transformer compartments.
Almost everywhere on our system I consider opening a door not an action that can cause an arc flash. As soon as someone crosses the plane of the door then I will say they need to have the proper PPE. I do work for a utility so the 70E standard does not apply for most of my work.
In this case the 70E standard does apply.
The equipment in question is a 24kV/480V pad mount transformer 1000kva, no exposed conductor on the 24kV side, exposed connection pad on the 480V side where the cables bolt to.
When I look at the risk register for this it seems very unlikely that an arc flash could occur.
What has your position been on this?
If I look at this scenario and determine the risk is low do I have to wear PPE specifically for opening the cabinet door?
Thanks for your input,
The task I am most interested in is: Opening voltage transformer or control power transformer compartments.
Almost everywhere on our system I consider opening a door not an action that can cause an arc flash. As soon as someone crosses the plane of the door then I will say they need to have the proper PPE. I do work for a utility so the 70E standard does not apply for most of my work.
In this case the 70E standard does apply.
The equipment in question is a 24kV/480V pad mount transformer 1000kva, no exposed conductor on the 24kV side, exposed connection pad on the 480V side where the cables bolt to.
When I look at the risk register for this it seems very unlikely that an arc flash could occur.
What has your position been on this?
If I look at this scenario and determine the risk is low do I have to wear PPE specifically for opening the cabinet door?
Thanks for your input,