doopedeng
Mechanical
- May 31, 2006
- 19
Hi All,
I have a vertical grease duct serving commercial kitchen equipment that is 18x30 running up through 5 stories to the roof and wondered if that is too small to permit "personnel entry" for cleaning as per Section 7.4.2.1, Vertical Ducts in NFPA 96-2004, or elsewhere? I.e., will I need to install access hatches on each floor instead?
Thanks in advance.
Dooped
I have a vertical grease duct serving commercial kitchen equipment that is 18x30 running up through 5 stories to the roof and wondered if that is too small to permit "personnel entry" for cleaning as per Section 7.4.2.1, Vertical Ducts in NFPA 96-2004, or elsewhere? I.e., will I need to install access hatches on each floor instead?
Thanks in advance.
Dooped