PagoMitch
Mechanical
- Sep 18, 2003
- 68
I am designing a couple small Med Gas Storage Rooms in a Hospital; (4) K cylinders each of N2 and CO2 (about 300 ft^3 each tank, 1200 ft^ 3 each room, 2400 ft^3 on this floor). These will be in separate rooms, although it is technically not required.
NFPA 99 2018 requires 1-hr walls, with 45-minute door and opening protection. This is in spite of 1-hr walls NOT needing protection (fire dampers) per NFPA. OK, so be it.
My question is on the exhaust:
Ducts down to one foot from the floor - no problem.
Exhaust at 1 CFM/5 ft^3 tank volume - no problem.
Non-combustible Exhaust Duct - no problem.
However... "Para 9.3.6.5.3.5: Dedicated exhaust systems shall not be required, provided that the system does not connect to spaces that contain combustible or flammable materials". OOPS, problem. This was going to connect to the Central Exhaust System, a nominal 5000 CFM Fan that serves roughly 16000 SF.
I cannot think of any enclosed area, anywhere (except for maybe an empty prison cell), that would not contain "combustible or flammable materials". Papers on a desk, a wall calendar, seat cushions, a wooden desk, wooden filing cabinets, manilla folders, the paper covering on an exam table, paper towels in the bathroom, cardboard boxes in the Janitors Closet holding cleaning supplies, and even the paper bags from In-N-Out burger would all be combustible, with the In-N-Out bag in particular (probably) being flammable due to the grease coating.
The way this is written, EVERY Med Gas Storage Room, even those at a miniscule 12 SF would require a dedicated Exhaust System.
I did try looking at definitions for "combustible or flammable materials" in NFPA, hoping it would be defined as Types of Construction - no such luck.
Am I missing something, or is this paragraph as literal - and inane - as it appears?
TIA.
NFPA 99 2018 requires 1-hr walls, with 45-minute door and opening protection. This is in spite of 1-hr walls NOT needing protection (fire dampers) per NFPA. OK, so be it.
My question is on the exhaust:
Ducts down to one foot from the floor - no problem.
Exhaust at 1 CFM/5 ft^3 tank volume - no problem.
Non-combustible Exhaust Duct - no problem.
However... "Para 9.3.6.5.3.5: Dedicated exhaust systems shall not be required, provided that the system does not connect to spaces that contain combustible or flammable materials". OOPS, problem. This was going to connect to the Central Exhaust System, a nominal 5000 CFM Fan that serves roughly 16000 SF.
I cannot think of any enclosed area, anywhere (except for maybe an empty prison cell), that would not contain "combustible or flammable materials". Papers on a desk, a wall calendar, seat cushions, a wooden desk, wooden filing cabinets, manilla folders, the paper covering on an exam table, paper towels in the bathroom, cardboard boxes in the Janitors Closet holding cleaning supplies, and even the paper bags from In-N-Out burger would all be combustible, with the In-N-Out bag in particular (probably) being flammable due to the grease coating.
The way this is written, EVERY Med Gas Storage Room, even those at a miniscule 12 SF would require a dedicated Exhaust System.
I did try looking at definitions for "combustible or flammable materials" in NFPA, hoping it would be defined as Types of Construction - no such luck.
Am I missing something, or is this paragraph as literal - and inane - as it appears?
TIA.