Standard for the Installation of Stationary Pumps for Fire Protection[/i], 2010 Edition]
4.31 Break Tanks.
4.31.3 Refill Mechanism. The refill mechanism shall be listed and arranged for automatic operation.
4.31.3.1 If the break tank capacity is less than the maximum system demand for 30 minutes, the refill mechanism shall meet the requirements in 4.31.3.1.1 through 4.31.3.1.5.
4.31.3.1.1 Dual automatic refill lines, each capable of refilling the tank at a minimum rate of 150 percent of the fire pump(s) capacity, shall be installed.
4.31.3.1.2 If available supplies do not permit refilling the tank at a minimum rate of 150 percent of the rated pump capacity, each refill line shall be capable of refilling the tank at a rate that meets or exceeds 110 percent of the maximum fire protection system design flow.
4.31.3.1.3 A manual tank fill bypass designed for and capable of refilling the tank at a minimum rate of 150 percent of the fire pump(s) capacity shall be provided.
4.31.3.1.4 If available supplies do not permit refilling the tank at a minimum rate of 150 percent of the rated pump capacity, the manual fill bypass shall be capable of refilling the tank at a rate that meets or exceeds 110 percent of the maximum fire protection system design flow.
4.31.3.1.5 A local visible and audible low liquid level signal shall be provided in the vicinity of the tank fill mechanism.
4.31.3.2 If the break tank is sized to provide a minimum duration of 30 minutes of the maximum system demand, the refill mechanism shall meet the requirements in 4.31.3.2.1 through 4.31.3.2.5.
4.31.3.2.1 The refill mechanism shall be designed for and capable of refilling the tank at 110 percent of the rate required to provide the total fire protection system demand [110% × (Total Demand −Tank Capacity) / Duration].
4.31.3.2.2 A manual tank fill bypass shall be designed for and capable of refilling the tank at 110 percent of the rate required to provide the total fire protection system demand [110% × (Total Demand −Tank Capacity) / Duration].
4.31.3.2.3 The pipe between the municipal connection and the automatic fill valve shall be installed in accordance with NFPA 24, Standard for the Installation of Private Fire Service Mains and Their Appurtenances.
4.31.3.2.4 The automatic filling mechanism shall be maintained at a minimum temperature of 40°F (4.4°C).
4.31.3.2.5 The automatic filling mechanism shall activate a maximum of 6 in. (152 mm) below the overflow level.
4.31.4 Installation Standard. The break tank shall be installed in accordance with NFPA 22, Standard for Water Tanks for Private Fire Protection.