Hi there, I'm asked to work on a spreadsheet to calculate the savings on AC night setback during summer. What would be the best method I should use instead of "1% savings per 1F setback".

Thanks in advance.
 
Replies continue below

Recommended for you

The website makes many, many assumptions about building construction, orientation, climate and etc.

Wrong assumptions make wrong conclusions......
 
The energy saved in any period of time is:

BTU = UA[(Tout-Tin)-setback]*time

If time is an hour, and you have hourly temperature bin data, you're done.

 