jerseyshore
Structural
- May 14, 2015
- 858
Was just sent a few photos of these pile caps pre-concrete pour. All but one is a single pile cap (the other is a poorly spaced double pile cap as you can see). These are placed along the front of a house supporting a 1st and 2nd floor deck. We're in a flood zone also.
Pretty obvious that not only is the rebar basically resting on the sand, but the piles have none inches of embedment into these caps.
The catch is that they already poured these and the building inspector is annoyed at the builder for pouring before they got inspected. He also wants the builder to rip them out because he didn't field treat the cut ends (which is never done, but is technically in the code [AWPA M4]). The architect who did the plans (and the crappy detail below) wants no part of this so they asked me if I can write the letter saying things are A-OK.
Thoughts here? There is very little load, but you gotta have some embedment right? Do I really take on the liability for this mess?
Pretty obvious that not only is the rebar basically resting on the sand, but the piles have none inches of embedment into these caps.
The catch is that they already poured these and the building inspector is annoyed at the builder for pouring before they got inspected. He also wants the builder to rip them out because he didn't field treat the cut ends (which is never done, but is technically in the code [AWPA M4]). The architect who did the plans (and the crappy detail below) wants no part of this so they asked me if I can write the letter saying things are A-OK.
Thoughts here? There is very little load, but you gotta have some embedment right? Do I really take on the liability for this mess?