Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations GregLocock on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

No load current of asynchronous motors

Status
Not open for further replies.

koruma

Electrical
Dec 28, 2001
19
What percentage of full load current is considered normal for no load conditions in squirrel cage induction motors?
 
Replies continue below

Recommended for you

No load current magnitude varies from approx 20%-60%, with low speed motors generally being closer to 60% and 2-pole motors generally being closer to 20%.
 
Just to add a note to your response, Electricpete, the no-load current is mainly reactive. There is not much difference between the no-load & the full load reactive current, which is the motor magnetizing current.
 
OK, jbartos, I'll bite on this one.
Your suggested links lead to -
a) - A manufacturer of small, special purpose DC motors
b) - The manual for a variable speed drive for elevator applications.

What, precisely, do these links have to do with the question in hand, which relates to the no-load current of squirrel cage induction motors?

Also, note that the power factor at no-load will tend to be be LOW, not high.
 
jbartos -
On re-reading the above, it comes to me that what you meant was that for a no-load current of 20% or less, the full load power factor would be extremely high (around 0.98). I agree with this, but still question the relevance of the links.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor