constantlylearning
Electrical
- Jan 5, 2006
- 38
We are currently trying to trouble-shoot a differential circuit on a delta-delta power transformer and are experiencing a strange phenomenon. We are consistently seeing a 10° to 15° phase shift between the HV and the LV windings of the transformer (measuring from the HV and LV CT's). To the best of my knowledge, there should be no phase shift between the HV side and the LV side of the transformer. For reference, the CT's are wye-connected and are made up outside the delta on the HV and LV windings. The HV CT's are located on the HV bushings of the transformer. The LV CT's are located in an adjacent switchgear cabinet about 20 feet away from the transformer.
While trouble-shooting a previous differential trip (which we do not believe is related), we noticed a small amount of differential current on our differential relay. At first, we suspected that we had made an error in the magnitude of the correction factor between the HV and LV side of the transformer. Eventually, we wound up installing a digital fault recorder and discovered that the differential current is not due to a magnitiude error. Instead, it seems to be due to a phase shift between the HV winding and the LV winding. In my expereience, you might expect to see up to ~1° phase shift due to CT error, but I think 15° would be unheard of.
If memory serves, current in the HV and LV windings of each phase of a power transforer should always be in phase or 180° out of phase, depending on the winding configuration. If that is the case, the winding currents on the HV and LV winding should sum in an identical manner at the delta corners in each of their respective windings. So, I believe the phases currents between the HV and LV of a delta-delta should always be in phase, unless there is some kind of problem within the transformer. However, this phases angle shift we are seeing is balanced across all three phases, so I don't think this is a fault.
Incidentally, when installing the fault recorder, we also picked up an additional set of CT's on the LV bushings of the transformer (in addition to those in the adjacent switchgear) to create a second differential zone. Both sets of LV CT's agree.
Also, we believe the differential trip mentioned earlier was due to a contamination problem in the LV bus duct. That trip was a phases-phase fault and was not exhibiting the same type of symptoms we see here.
While trouble-shooting a previous differential trip (which we do not believe is related), we noticed a small amount of differential current on our differential relay. At first, we suspected that we had made an error in the magnitude of the correction factor between the HV and LV side of the transformer. Eventually, we wound up installing a digital fault recorder and discovered that the differential current is not due to a magnitiude error. Instead, it seems to be due to a phase shift between the HV winding and the LV winding. In my expereience, you might expect to see up to ~1° phase shift due to CT error, but I think 15° would be unheard of.
If memory serves, current in the HV and LV windings of each phase of a power transforer should always be in phase or 180° out of phase, depending on the winding configuration. If that is the case, the winding currents on the HV and LV winding should sum in an identical manner at the delta corners in each of their respective windings. So, I believe the phases currents between the HV and LV of a delta-delta should always be in phase, unless there is some kind of problem within the transformer. However, this phases angle shift we are seeing is balanced across all three phases, so I don't think this is a fault.
Incidentally, when installing the fault recorder, we also picked up an additional set of CT's on the LV bushings of the transformer (in addition to those in the adjacent switchgear) to create a second differential zone. Both sets of LV CT's agree.
Also, we believe the differential trip mentioned earlier was due to a contamination problem in the LV bus duct. That trip was a phases-phase fault and was not exhibiting the same type of symptoms we see here.