gautamraj
Structural
- Jan 25, 2012
- 1
I have a project in which the contractor notched several existing floor joists to install new pipes. The floor joists consists of full 2x10 at 16” on center. The joist spans are 10’ and 14’ with a mid support. The joists are continuous over the mid support. The notch is within the mid 1/3 span in the 10 foot span. The depth of the notch varies but is less than 1.5”.
Because of the electrical wires already installed, the contractor does not want to sister a new 2x8 (2x8 is adequate for bending and deflection). I am thinking of jacking up the joist to counter the dead load deflection and installing a Simpson 12 gage metal strap across the notch at the bottom face of the joist.
Your comments and insight would be appreciated.
Gautam
Because of the electrical wires already installed, the contractor does not want to sister a new 2x8 (2x8 is adequate for bending and deflection). I am thinking of jacking up the joist to counter the dead load deflection and installing a Simpson 12 gage metal strap across the notch at the bottom face of the joist.
Your comments and insight would be appreciated.
Gautam