Number of breaker operations possible...

Status
Not open for further replies.

tlr7616

Electrical
Feb 21, 2007
8
US
I am trying to find out what the typical number of open/close/open/close operations is possible for a high voltage circuit breaker (>69 kV). Many of the higher voltage circuit breakers are blast type breakers and are limited to just a few operations until the compressor can recharge. In my experience no more than four operations is the norm--what is the word on this from you folks?

Thanks!
 
Replies continue below

Recommended for you

Refer to the manufacturer literature. If there is an expected number of operations, it will be in there.

I seem to remember a certain make of hydraulically operated OCB that was expected to make three operations from fully charged if power to the pump was turned off, but it's been some years since I worked with that. I twas in their literature, though.


old field guy
 
You might want to check the ANSI C37 standards - there may be some minimum requirements in there.
 
Our 115 kV breakers range from open-close-open up to at least three cycles. C37.04 has a table requiring various amounts of stored energy, depending on how long the charging time is. It ranges from OCO for a 15 second recharge to five CO cycles if charging takes longer than 30 minutes.
 