rockman7892
Electrical
- Apr 7, 2008
- 1,171
I have been doing some investigating as of lately on the number of starts that are permissible on an MV motor. From what I see this is dictated by the NEMA MG-1 standard which says the motor should be capable of 2 cold starts and 1 hot start. I understand however that this is usually a minimum requirment and is one that is not closely regulated.
For a given motor datasheet which has a listing of 2 cold starts and 1 hot start is this a minimum that the manufacturer is stating the motor is capable of meeting or is this usually a maximum? Or this somewhat of a gray area?
I also understand that the thermal capacity used during a start depends on the inertia of the load or how much of the load is present. So lets say that the motor datasheets lists the 2cold 1hot rating for a given inertia. So esentially when starting this inertia you would expect to use about 50% thermal capacity on each start thus allowing only 2 consecutive starts from cold before 100% thermal capacity was used.
Lets say however that the load being started in much less and has a much smaller inertia than is listed on the motor datasheet (maybe 1/4 of that listed.) With this case when starting the motor we are only using about 10% of the motors thermal capacity. If only using this 10% at a reduced load, would this allow for more than 2 cold starts on a motor if required. For instance if we for some reason needed 4 starts on the motor would this be allowable since with each start at 10% we would only use 40% of the motors thermal capacity?
If this is the case then I would think the start inhibit function of a protecive relay would be the best option for determining how much thermal capacity it takes to start the motor compared to how much thermal capacity is avaliable in order to determine how may starts are allowed as opposed to limiting it to some hard number.
I wanted to hear what others thoughts and experiences are.
Thanks
For a given motor datasheet which has a listing of 2 cold starts and 1 hot start is this a minimum that the manufacturer is stating the motor is capable of meeting or is this usually a maximum? Or this somewhat of a gray area?
I also understand that the thermal capacity used during a start depends on the inertia of the load or how much of the load is present. So lets say that the motor datasheets lists the 2cold 1hot rating for a given inertia. So esentially when starting this inertia you would expect to use about 50% thermal capacity on each start thus allowing only 2 consecutive starts from cold before 100% thermal capacity was used.
Lets say however that the load being started in much less and has a much smaller inertia than is listed on the motor datasheet (maybe 1/4 of that listed.) With this case when starting the motor we are only using about 10% of the motors thermal capacity. If only using this 10% at a reduced load, would this allow for more than 2 cold starts on a motor if required. For instance if we for some reason needed 4 starts on the motor would this be allowable since with each start at 10% we would only use 40% of the motors thermal capacity?
If this is the case then I would think the start inhibit function of a protecive relay would be the best option for determining how much thermal capacity it takes to start the motor compared to how much thermal capacity is avaliable in order to determine how may starts are allowed as opposed to limiting it to some hard number.
I wanted to hear what others thoughts and experiences are.
Thanks