Number of Man doors needed into a MCC room. 1

Status
Not open for further replies.

wgrjr

Industrial
Jun 11, 2012
4
Is there a requirement for the number of man doors to be supplied for access into a room containing a MCC center ?
 
Replies continue below

Recommended for you

I am sure everyone would agree to that educated answer, I am looking to see if anyone knows of a requirement to provide two (2) separate entrances to the room.
 
What is an MCC Center??

I prefer two doors to any sizable room - not closets - for example.

What if there is a fire right in front of the ONLY door out?? With two doors chances that both would be blocked are minimal - I would think - esp if they are nearly opposite each other. If that happens - the whole room is probably on fire already - and well - Good Luck!!
 
I also prefer two doors, But I am looking for a code stating how many access doors are required
 
NEC 110.26 (C) Two doors are required for rooms with switchboards/MCC/etc 1200 A or more and over 6 feet long. There is an exception if double the required working space is provided in front of the board.
 
Thanks dpc that is what I have been looking for.
 
@dpc, there is a grandfather clause with that correct? Do you know what year that requirement was added?
 
I'm late getting back to this, but everything in the NEC has a grandfather clause - nothing is retroactive.

That requirement has been in the NEC a long time. It's in the 1999 NEC. The basic requirement is in the 1978 NEC, except it adds the caveat "where reasonably practical". I think these weasel words were removed in the early 1980's.

 