I have the exact same situation that came up in a previous thread regarding combination manual-wet standpipe systems in NYC.
Basically, our building type requires a standpipe system based on floor area sizes (not a covered mall). It is a low-rise structure so manual-wet is the minimum requirement for the standpipe system. We are utilizing a combination sprinkler/standpipe system but require a pump to meet the sprinkler system demand only.
Since the pump is only required to meet the sprinkler system demand, we would like to call it a "sprinkler booster pump" in lieu of a "fire pump" so we can avoid the requirement for two separate water mains off two separate streets. However, there are questions as to whether or not a booster pump can technically feed into a combination sprinkler/standpipe system.
The only water supply requirement for a manual-wet standpipe system other than the FDC is a small connection for the purpose of keeping the pipe filled with water. Obviously, a booster pump will achieve this requirement and since the pump has a bypass, it will keep the standpipes filled even if the pump ever goes down.
Has anyone ever ran into this situation before in this jurisdiction? Can you have a combination manual-wet standpipe system supplied from a sprinkler booster pump with a single underground supply line in NYC? Or, will this "pump" need to meet all the "fire pump" requirements which includes two separate undergrounds from two separate streets?
Basically, our building type requires a standpipe system based on floor area sizes (not a covered mall). It is a low-rise structure so manual-wet is the minimum requirement for the standpipe system. We are utilizing a combination sprinkler/standpipe system but require a pump to meet the sprinkler system demand only.
Since the pump is only required to meet the sprinkler system demand, we would like to call it a "sprinkler booster pump" in lieu of a "fire pump" so we can avoid the requirement for two separate water mains off two separate streets. However, there are questions as to whether or not a booster pump can technically feed into a combination sprinkler/standpipe system.
The only water supply requirement for a manual-wet standpipe system other than the FDC is a small connection for the purpose of keeping the pipe filled with water. Obviously, a booster pump will achieve this requirement and since the pump has a bypass, it will keep the standpipes filled even if the pump ever goes down.
Has anyone ever ran into this situation before in this jurisdiction? Can you have a combination manual-wet standpipe system supplied from a sprinkler booster pump with a single underground supply line in NYC? Or, will this "pump" need to meet all the "fire pump" requirements which includes two separate undergrounds from two separate streets?