I have the exact same situation that came up in a previous thread regarding combination manual-wet standpipe systems in NYC.
Basically, our building type requires a standpipe system based on floor area sizes (not a covered mall). It is a low-rise structure so manual-wet is the minimum requirement for the standpipe system. We are utilizing a combination sprinkler/standpipe system but require a pump to meet the sprinkler system demand only.

Since the pump is only required to meet the sprinkler system demand, we would like to call it a "sprinkler booster pump" in lieu of a "fire pump" so we can avoid the requirement for two separate water mains off two separate streets. However, there are questions as to whether or not a booster pump can technically feed into a combination sprinkler/standpipe system.

The only water supply requirement for a manual-wet standpipe system other than the FDC is a small connection for the purpose of keeping the pipe filled with water. Obviously, a booster pump will achieve this requirement and since the pump has a bypass, it will keep the standpipes filled even if the pump ever goes down.

Has anyone ever ran into this situation before in this jurisdiction? Can you have a combination manual-wet standpipe system supplied from a sprinkler booster pump with a single underground supply line in NYC? Or, will this "pump" need to meet all the "fire pump" requirements which includes two separate undergrounds from two separate streets?
 
Replies continue below

Recommended for you

No experience in NYC, but I have done this on several different projects not in NYC. It is still a UL Listed fire pump. But lets say the sprinkler demand is 300 gpm and the standpipe is 1000 gpm. I have put in a 300 gpm pump many times. You just upsize everything once you get to the point where the standpipes are.

Travis Mack
MFP Design, LLC
"Follow" us at
 
Thanks. That is the frustrating part. There is physically no difference between a "fire pump" & a "booster pump". The only thing that differentiates them is which system they serve. A "fire pump" implies that there is an automatic-wet standpipe inside the building so FDNY doesn't need to pump in through the FDC to meet the standpipe demand. A "booster pump" implies a manual-wet standpipe which tells FDNY they do need to pump in through the FDC to meet the standpipe demand.

It truly is a matter of semantics but it can have huge repercussions on the basic requirements for the system (i.e., two underground lines from two city streets). In any other jurisdiction, a pump serving a fire system is a "fire pump" but that is not the case in NYC; for whatever reason the differentiate between a booster pump & fire pump.

I was hoping that someone with experience in NYC would be able to answer whether or not a "sprinkler booster pump" could supply a combination manual-wet standpipe system or not.
 
Interesting the terminology.

I learned, and still say, A "Booster Pump" connects to a city supply.
A "Fire Pump" is fed from a tank.

Guess NYC has different meaning..

R/
Matt
 