Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

O86 Built up beam Moment Capacity

Status
Not open for further replies.

murphy89

Structural
Mar 24, 2022
15
0
0
CA
Hello,

I am working through a spreadsheet written a number of years ago (probably early 2000's) by another engineer that calculates the number of plies of various lumber sizes to satisfy load, span, and bearing length criteria that I input.

One section of their spreadsheet under a title they call "Load Sharing" applies a factor of 0.9090909090 to the moment capacity of a built-up beam if there are 3 or more plies in the beam. I can't find any reference to this in my O86-2010. Is this something that used to be in the O86 code and no longer exists? Does anyone know?

Thanks!
 
Replies continue below

Recommended for you

Without seeing how it is specifically applied in the formula, it sounds like they're dividing by the system factor Kh of 1.1 for built-up beams. See Table 6.4.4 (that's in the O86-14 but I feel it's likely similar in the 2010). 1/1.1=0.9090909.
 
Status
Not open for further replies.
Back
Top