Is there any NFPA 13 code section I can refer to avoid sprinkler heads underneath the sunshade? (Please see attached sketch)
A room, 11’-0” ceiling height, light hazard occupancy has aluminum sunshade in the window. The sunshade is 3’-10” below the ceiling and extends 2’-11” into the room from the window. NFPA 13 2010 Section 8.6.5.3.3 states, sprinkler shall be installed under fixed obstructions over 4ft. Can any of the sections be applied to avoid sprinklers underneath the shade?
The maximum allowable distance of deflector above the bottom of obstruction per table 8.6.5.1.2 is 35 in. The distance from the ceiling to the sunshade is 46 in. also “D” in Fig. 8.6.5.1.2(b) is greater than 30” so I can’t apply thee basic obstruction rules.
A room, 11’-0” ceiling height, light hazard occupancy has aluminum sunshade in the window. The sunshade is 3’-10” below the ceiling and extends 2’-11” into the room from the window. NFPA 13 2010 Section 8.6.5.3.3 states, sprinkler shall be installed under fixed obstructions over 4ft. Can any of the sections be applied to avoid sprinklers underneath the shade?
The maximum allowable distance of deflector above the bottom of obstruction per table 8.6.5.1.2 is 35 in. The distance from the ceiling to the sunshade is 46 in. also “D” in Fig. 8.6.5.1.2(b) is greater than 30” so I can’t apply thee basic obstruction rules.