Dear sirs
Does anybody knows if table 8.6.5.1.2 from NFPA 13 Ed 2016 applies to in-rack sprinklers?
Ítem 8.13.5 Obstruction to in-rack discharge says: "In-rack sprinklers shall not be required to meet the obstruction criteria and clearance from storage requirements of Section 8.5".
No reference in 8.13.5 to 8.5 but since section 8.5 is general, and 8.6 particular for standar spray, it is not clear if the table applies.
Does anybody knows if table 8.6.5.1.2 from NFPA 13 Ed 2016 applies to in-rack sprinklers?
Ítem 8.13.5 Obstruction to in-rack discharge says: "In-rack sprinklers shall not be required to meet the obstruction criteria and clearance from storage requirements of Section 8.5".
No reference in 8.13.5 to 8.5 but since section 8.5 is general, and 8.6 particular for standar spray, it is not clear if the table applies.