MrStohler
Structural
- May 1, 2001
- 81
Thanks in advance, I would appreciate some feedback about interpreting the 1997 AISC Seismic Provisions.
The project in question is covered by IBC 2000 and is in Seismic Design Catagory D. As a result the 1997 AISC Seismic Provisions also apply. The structure is to be designed as a ordinary concentrically braced frame (this question would also aplly to a SCBF). Most of the vertical bracing will be wide flange sections turned so the flange surfaces are vertical, which are connected to a gusset with 4 "claw" angles at thw WF's web (long spans make double angle bracing less feasible and welded HSS bracing is not an option).
AISC-97 SP Section 14.3c indicates that the connection needs to provide flexural strength of at least 1.1*Ry*Mp in the "direction" of the brace buckling. I'm OK with this concept, but it creates alot of work (our firm designs all connections, this is not left to a detailer). It could lead to a very complicated analysis if the buckling is out of plane wrt the gusset, but the design configuration could address this.
There is an exception to meeting the Flexural Strength requirements:
"Exception: Bracing connections that meet the requirements in Section 14.3b., that can accommodate the inelastic rotations associated with brace post-buckling deformations, and that have a design strength that is at least equal to the nominal compressive strength Fcr*Ag of the brace are permitted."
Finally, the question: The first and last items of the exception can be addressed easliy but what would be an appropriate method to evaluate whether the connection can accommodate the inelastic rotations associated with brace post-buckling deformations?
Thanks again.
The project in question is covered by IBC 2000 and is in Seismic Design Catagory D. As a result the 1997 AISC Seismic Provisions also apply. The structure is to be designed as a ordinary concentrically braced frame (this question would also aplly to a SCBF). Most of the vertical bracing will be wide flange sections turned so the flange surfaces are vertical, which are connected to a gusset with 4 "claw" angles at thw WF's web (long spans make double angle bracing less feasible and welded HSS bracing is not an option).
AISC-97 SP Section 14.3c indicates that the connection needs to provide flexural strength of at least 1.1*Ry*Mp in the "direction" of the brace buckling. I'm OK with this concept, but it creates alot of work (our firm designs all connections, this is not left to a detailer). It could lead to a very complicated analysis if the buckling is out of plane wrt the gusset, but the design configuration could address this.
There is an exception to meeting the Flexural Strength requirements:
"Exception: Bracing connections that meet the requirements in Section 14.3b., that can accommodate the inelastic rotations associated with brace post-buckling deformations, and that have a design strength that is at least equal to the nominal compressive strength Fcr*Ag of the brace are permitted."
Finally, the question: The first and last items of the exception can be addressed easliy but what would be an appropriate method to evaluate whether the connection can accommodate the inelastic rotations associated with brace post-buckling deformations?
Thanks again.