Hello everyone!
I have a 3 phase 208v buss with no neutral or ground (using case ground). I have a Buss plug connected with 3 phase wires (lets say A,B,C)& a ground wire going to a transformer. The transformer is 240v primary - 208v secondary. Were back feeding the transformer as we have 208v & need 240v. At the transformer I tied the ground wire from the buss plug to the ground lug on the transformer frame. The primary feed wires from the buss plug are connected phases A,B,C to X1,X2,X3, nothing is tied to X0. The secondary wires connected to H1,H2,H3 at the transformer and to the 3 phase breaker in the panel box. I ran a ground from the transformers ground lug to the panel boxes grounding bar. I installed the panel bonding screw to the grounding bar.
Reading between phases I have the correct voltages of 240v & 208v. X1,X2,X3 to ground in the transformer is 120v. H1(A)-gnd = 160v, H2(B)-gnd =98v, H3(C)-gnd =157v in the transformer or panel. I was expecting to see 120v!
Does anyone know why? Should I have XO connected to ground?
I have a 3 phase 208v buss with no neutral or ground (using case ground). I have a Buss plug connected with 3 phase wires (lets say A,B,C)& a ground wire going to a transformer. The transformer is 240v primary - 208v secondary. Were back feeding the transformer as we have 208v & need 240v. At the transformer I tied the ground wire from the buss plug to the ground lug on the transformer frame. The primary feed wires from the buss plug are connected phases A,B,C to X1,X2,X3, nothing is tied to X0. The secondary wires connected to H1,H2,H3 at the transformer and to the 3 phase breaker in the panel box. I ran a ground from the transformers ground lug to the panel boxes grounding bar. I installed the panel bonding screw to the grounding bar.
Reading between phases I have the correct voltages of 240v & 208v. X1,X2,X3 to ground in the transformer is 120v. H1(A)-gnd = 160v, H2(B)-gnd =98v, H3(C)-gnd =157v in the transformer or panel. I was expecting to see 120v!
Does anyone know why? Should I have XO connected to ground?