DiegoMartinez

Petroleum
Jul 1, 2006
65
Hi Guys,
We have 4 bottles of odourant on site. Nitrogen blanketing line is supplied with 100 KPag to each bottle. The distance between bottles to the odourant cabinet where 4 high pressure pumps are, is nearly 3 meters. Recently we had the problem of pump lock due to vapour existence in the line. The odourant supply piping is flexible hose and 3/8" ss tubing. Can anybody advise what is the problem? Is there potential the nitrogen dissolve in Odourant? What should be the nitrogen pressure? Is the flex. hose good for this application?
 
Replies continue below

Recommended for you

hello,

I assume the vapor pressure of the odourant is high, did you check the NPSH Available versus the Required?

Regards,
roker
 