A customer of mine wants to start a sequence utilizing two timers in series once the "Wireless Controller" contact is closed. I did the logic in PLC but then the customer changed his mind when he found out how much it was going to cost for a PLC brick. So he asked if I can do a hardwire system. The sequence of operations is as follows: wireless controller contact is closed which then starts the off-delay timer #1 to energize a ball valve for 30 seconds. Once the 30 seconds is over, off-delay timer #2 needs to then start its timer for 5 seconds to energize the flush valve. I am stuck on how to make this happen with the hardwire system that's being requested. Any advice is appreciated.
 
Replies continue below

Recommended for you

Put the second timer in parallel with the ball valve or use a second set of contacts from the first timer.

--------------------