RMERMP

Mechanical
Feb 22, 2016
45
0
0
PH
I'm trying to find a minimum area requirement of office occupancy that need to be protected by automatic sprinkler system? can anyone direct me to a code regarding this? im reading IFC now but i cant find the requirements in Group B occupancy. for reference purposes only. thanks
 
Replies continue below

Recommended for you

For B ,,,Without more details base ibc and ifc only require it in

903.2.2 Group B ambulatory health care facilities. An automatic sprinkler system shall be installed throughout all fire areas containing a Group B ambulatory health care facility occupancy when either of the following conditions exists at any time: [F]
1. Four or more care recipients are incapable of self-preservation.
2. One or more care recipients who are incapable of self-preservation are located at other than the level of exit discharge serving such an occupancy.


There could be other factors that might require one
 
I'm assuming your using the 2012 IFC. A Group B occupancy doesn't require automatic sprinklers unless it is a high rise building, is more than 55 feet above the lowest level of fire department access and has an occupant load > 30 or it's an ambulatory care facility.
 